Posted: Fri Mar 01, 2013 10:10 am
I have received a number of part L models from my colleague who routinely imports the annual profile template (Mod) office controlled lighting [LICO] and applies it as the dimming profile in rooms where there are dimmable fittings. Is this correct?
I see this as fundamentally wrong as the profile dims all lights within the zone to around 30% for the majority of the year giving fantastic energy savings. Where in reality most cases have just the first row of fittings nearest the windows as dimmable. (these are side light buildings without roof lights in the zone under consideration)
My preference is to use the NCM photoelectric controls
I see this as fundamentally wrong as the profile dims all lights within the zone to around 30% for the majority of the year giving fantastic energy savings. Where in reality most cases have just the first row of fittings nearest the windows as dimmable. (these are side light buildings without roof lights in the zone under consideration)