In construction I see Total Coefficient for glazing after deriving parameter, in general or theory, SHGC = SC x 0.87. So total Coefficient in VE equivalent SHGC or SC ?
Thanks.
SHGC and Total Shading Coefficient
Re: SHGC and Total Shading Coefficient
The SHGC is calculated as follows:
SHGC = Total shading coefficient * 0.87
This complies with NFRC. If you wish to view the calculated SHGC then you can do so by switching the U-Value method to ASHRAE, you’ll then be able to view the SHGC in derived parameters.
SHGC = Total shading coefficient * 0.87
This complies with NFRC. If you wish to view the calculated SHGC then you can do so by switching the U-Value method to ASHRAE, you’ll then be able to view the SHGC in derived parameters.