Radiant heat fraction for Under floor heating
Posted: Mon Mar 04, 2013 10:30 am
by ColinR
Hi guys,
Query about the radiant fraction setting when modelling underfloor heating.
Default settign for all systems is 20% (0.2), am I right in saying that this means that of the heat output from the system, 20% of it is radiant and the other 80% is assumed to be conductive and/or convective?
I may be wrong but I would have thought that Undefloor heating would be mostly conductive and radiative. I was thinking perhaps a figure of 0.5?
Is there any IES documentation that explains the operation of this function clearly?
cheers,
C
Re: Radiant heat fraction for Under floor heating
Posted: Mon Mar 04, 2013 10:39 am
by PCully
Hi,
this is from the ApacheView user guide (can be accessed via the Help >> User Guides
http://www.iesve.com/downloads/help/ve2 ... heView.pdf)
Heating plant radiant fraction
The fraction of the heating plant’s output that is in the form of radiant, rather than convected, heat. A value of 0.0 is appropriate for warm air heating and a value of 0.9 for high-temperature radiant heaters. See Table 13 for further guidance.
Phil
Re: Radiant heat fraction for Under floor heating
Posted: Mon Mar 04, 2013 10:54 am
by ColinR
Top man Phil, thanks for that.
Re: Radiant heat fraction for Under floor heating
Posted: Mon Mar 04, 2013 11:15 am
by ColinR
Sorry, where can I get access to "Table 13"?

Re: Radiant heat fraction for Under floor heating
Posted: Mon Mar 04, 2013 1:55 pm
by PCully

these really to need to be made as hyperlinks, you can access it in the document Apache Tables (also accessible via Help >> User Guides >> Thermal section).
I think IES get a hard time for "lack of documentation" but we have been working to correct this lately, I'm finding lots of the answers to things people ask us is actually in the user guides already and they are available as an excellent resource to all. Maybe it's the "marketing" and naming that needs revised a touch.
http://www.iesve.com/downloads/help/ve2 ... Tables.pdf
Phil
Re: Radiant heat fraction for Under floor heating
Posted: Mon Mar 04, 2013 3:59 pm
by ColinR
Fantastic Phil, just what I needed. I was almost certain I could recall my Uni lecturer telling me to put in 0.5 for underfloor heating, obviously I should trust my memeory a bit more
Thanks for that,
Colin
Re: Radiant heat fraction for Under floor heating
Posted: Mon Mar 04, 2013 5:18 pm
by PCully
Never doubt your instincts!