Apache HVAC Fixed OA Percentage

Post by rms4000 »

Has anyone ever figured out how to fix the OA percentage of an air system? I'm trying to peg a system at 30%, but it seems like something out there is overrriding the system diagram.
Paul_Paterson
VE Newbie
VE Newbie
Posts: 1
Joined: Wed Jun 26, 2013 10:01 am

Re: Apache HVAC Fixed OA Percentage

Post by Paul_Paterson »

Yeah,

depending on your current network you may need to add an additional mixing damper set to simulate (as you need a separate set for each control type. Once you have done this add an independent controller with sensor set to sense main fan flowrate and set to 30% at the inlet to the mixing damper

Paul