Confusting ApacheHVAC 'Invalid configuration' error
Posted: Tue Apr 30, 2013 12:21 pm
I'm currently modeling a building which has two air handlers. I pulled in prototype system 05a, copied it, assigned the appropriate rooms to the multiplex and that's it.
The room loads run fine, but when I try to do system sizing runs (or do a network check), I get the following error:
The room loads run fine, but when I try to do system sizing runs (or do a network check), I get the following error:
What does that mean? The multiplex it refers to literally has the exact same layout as my other system, but that one works fine. What could be causing this error?Network is not valid. Reason:
Invalid configuration: Selected multiplex[ID: MU000101] contains a duct-only section, re-route this to be outside the multiplex. resizing the multiplex may help.