Modelling Underfloor Heating
Posted: Tue Jun 18, 2013 8:44 am
by Richardo1505
Hi all,
Can anyone offer some advise on how to model underfloor heating. Is it as simple as changing the room system radiant fraction (using a value of 0.5 as IES guidance)??????
Thanks Richard
Re: Modelling Underfloor Heating
Posted: Fri Jun 21, 2013 4:24 am
by Marc Jensen
Hey Richardo,
I have modelled the underfloor heating in a couple of ways, however the method that I found that gives me the most control over the design and performance of the underfloor heating was doing the following:
Move the building up 100mm and insert a sliver of all the rooms etc. To this set your 85W/m2 etc
that method is easy to control as you set up and individual system etc especially good if you want to test the system without removing any others.
Re: Modelling Underfloor Heating
Posted: Sat Jun 22, 2013 9:02 am
by Richardo1505
How interesting, thanks for this Marc, really hadn't though about that method