Error: Material CVTY0083 not found

Posted: Fri Nov 15, 2013 11:06 am
by simonemiri3
Hi,
I'm doing LEED certification, when I run Apache Sim appear one window with "Error: Material CVTY0083 not found".
The software generate this error only after importing Prototipe Data (ASHRAE Baseline).
Also if in building template manager I try to import external Template appear another one error window: "corrupt construction database:construction BSWAL42 refers to missing material CVTY0083. Please inform IES Ltd"

What's wrong?

Thanks in advance

Re: Error: Material CVTY0083 not found

Posted: Fri Nov 15, 2013 5:05 pm
by Terence
It’s caused by baseline wood framed walls. If this is a prm project, the walls should be metal framed so you should either delete these constructions or open each wood framed baseline construction and remove the composite layer. If you do need these constructions for the proposed perhaps, you can use the ASHRAE wizard in the tools menu of the constructions database to create it.

Just open the constructions database, look for any baseline construction with wood frame in the name, select using the check box and click delete or open each of them and delete the composite layer.

Re: Error: Material CVTY0083 not found

Posted: Mon Nov 18, 2013 11:35 am
by simonemiri3
I solved the problems!

Thanks,

Simone