Criterion 3 and transient spaces

Posted: Wed Feb 05, 2014 3:29 pm
by bootsam
Ive a transient space. Defined as a circulation area. According to Para4.44d of Part L2A these should be excluded. However it is still assessing the space and failing it. Its a foyer/lobby with a glazed part of its roof. This area should not be being considered amongst the checks. Whassup?

??

Re: Criterion 3 and transient spaces

Posted: Wed Feb 05, 2014 3:43 pm
by Terence
Is the space cooled? In accordance with the 2010 NCM modelling guide, ApacheSim Compliance only performs Criterion 3 check on applicable rooms, i.e it will only report results for rooms that are occupied or mechanically cooled.