hi , i have inputted all lighting as w/m2/100lux from the lighting calcualtions supplied by elec engineer ,this was done in ve compliance , now i need to do heat gains and i noticed that when i simply move to apache tab the ltg heat gains are as the template not as my room-by-room entered values from VE-compliance, is there a way i can have these already inputted values brought into heat gains calcs avoiding the double amount of work of inputting it once again.

apologies if the subject is covered elsewhere already

regards

andy
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: cibse heat gains

Post by Complex Potential »

This is a good question.

The answer is that yes you can transfer the figures but you need to do it by exporting the tabular room data for the entire model into excel from VE and then paste it back into the tabular room data in Apache. Make sure you alter the headings in excel to match those in Apache tabular data because they differ slightly from the VE version.

It might take you a couple of attempts to make it work but stick with it. Remember to include the Room ID column for all pasting because that's what IES uses to identify rooms.