coil contatc factor
Posted: Thu Feb 20, 2014 10:22 am
Hello,
I have some questions regarding the functioning of the software VE and the functioning of some HVAC components.
The Cooling coil component needs a parameter named “Coil Contact factor” to be defined.
This contact factor is used to describe the way air flows over the coil, and is used to calculate the balance of sensible to latent heat removal of the air passing over the coil. Several tests on this parameter show that reducing the contact factor implies increasing the Latent Load and the dehumidification.
Contact coil factor 0.1 0.5 0.7 0.91
Sensible (kW) 38.0 38.0 38.0 38.0
Latent (kW) 17.0 6.36 1.5 0.7
Latent/Sensible 45% 17% 4% 2%
If we look at the formula describing the contact factor, we observe that fixing the contact factor to one single value during all the simulation implies that the temperature of the Apparatus Dew Point (ADP) varies depending on the temperature of the air entering the cooling coil .
contact factor= (x1-x2)/(x1-x3)=(h1-h2)/(h1-h3)~(t1-t2)/(t1-t3)
I don’t understand how the ADP temperature is related to the Chilled water supply temperature and to the Delta T in the definition of the chilled loop.
Moreover, I tried to modify the value of the chilled water supply temperature and the value of the Delta T in the definition of the chilled loop, it doesn’t seem to have an impact on the Latent Loads. Only the contact coil factor changes the ratio Latent loads/Sensible Loads. How can it be explained?
Thank you very much for your attention,
Bests regards,
I have some questions regarding the functioning of the software VE and the functioning of some HVAC components.
The Cooling coil component needs a parameter named “Coil Contact factor” to be defined.
This contact factor is used to describe the way air flows over the coil, and is used to calculate the balance of sensible to latent heat removal of the air passing over the coil. Several tests on this parameter show that reducing the contact factor implies increasing the Latent Load and the dehumidification.
Contact coil factor 0.1 0.5 0.7 0.91
Sensible (kW) 38.0 38.0 38.0 38.0
Latent (kW) 17.0 6.36 1.5 0.7
Latent/Sensible 45% 17% 4% 2%
If we look at the formula describing the contact factor, we observe that fixing the contact factor to one single value during all the simulation implies that the temperature of the Apparatus Dew Point (ADP) varies depending on the temperature of the air entering the cooling coil .
contact factor= (x1-x2)/(x1-x3)=(h1-h2)/(h1-h3)~(t1-t2)/(t1-t3)
I don’t understand how the ADP temperature is related to the Chilled water supply temperature and to the Delta T in the definition of the chilled loop.
Moreover, I tried to modify the value of the chilled water supply temperature and the value of the Delta T in the definition of the chilled loop, it doesn’t seem to have an impact on the Latent Loads. Only the contact coil factor changes the ratio Latent loads/Sensible Loads. How can it be explained?
Thank you very much for your attention,
Bests regards,