Ground Contact Edge Insulation

Posted: Mon Mar 10, 2014 6:09 pm
by Nick
Does anyone know if this can be defined in IES? When following the 90.1 PRM Navigator there is a selection for finding "above ground" then the "ground contact" for surface assignment.

Very small parameter I know, but it exists in a lot of our construction documents and would like to make sure it's being properly accounted for if possible.

Thanks so much! :D

Nick

Re: Ground Contact Edge Insulation

Posted: Tue Mar 18, 2014 4:49 pm
by Megan
Nick,

Edge insulation is accounted for using the "Ground-contact U-value adjustment" in the Functional Settings of your floor construction. When you open up the adjustment dialog within the construction, you'll find there are 2 approaches for making the adjustment, the ASHRAE F-factor and the European norm, EN-ISO 13370. Which you use depends on where your project is located/what the purpose of the energy model is.

Thanks,
Megan

Re: Ground Contact Edge Insulation

Posted: Fri Mar 21, 2014 4:21 pm
by Nick
Great thanks Megan!