Air Exchanges
Posted: Tue Mar 25, 2014 8:53 am
by iwmech
A quick one, does anyone know what l/s.m²fac mean as a unit for air exchange flow rate?
Thanks in advance.
Re: Air Exchanges
Posted: Tue Mar 25, 2014 10:25 am
by Complex Potential
That just means that the flow rate is dependent upon the floor area of the room the air exchange is attached to.
So if you have a template with an air exchange set at 0.5 l/s.m2 and you apply that template to a room with 50m2 floor area, the flow rate for that room will be 0.5 x 50 = 25 l/s
CP
Re: Air Exchanges
Posted: Thu Mar 27, 2014 6:41 am
by iwmech
Hi CP,
Thanks for your response. Thought about it some more and I suspect that it actually means L/s per meter squared of facade? There is another option L/s.m^2 and I guess this is what you suggested.
Thank you.
Re: Air Exchanges
Posted: Thu Mar 27, 2014 10:07 am
by Complex Potential
Ah yes, I think you're right. That one is quite a new option I think but handy.