I'm not seeing any energy on the BRUKL for CHP. Ive added it via the renewables tab and ticked it via the NCM template manager. I'm running a LTHW with rads scheme and would expect to see CHP energy on the BRUKL but I am not. Am I being stoopid? 
Re: CHP
Figured it. Min output it shuts down before unit sees benefit as its so small.
I have an energy centre providing energy for 400+ dwellings and 1 small retail unit. Thus when I shove the huge 400kW CHP on, the min 0.5 is 200kW and my small load is too small to be seen.
Just posting this for others information.
I have an energy centre providing energy for 400+ dwellings and 1 small retail unit. Thus when I shove the huge 400kW CHP on, the min 0.5 is 200kW and my small load is too small to be seen.