Dear Team,
below error is observed when I start running the load calculation ; please help me to understand what was wrong?
'' Element CCR101 in room 'L0_ Vice Principal Office [L0VC000]' has no corresponding element in room ' L1_Post Holder [L1TR001]'
Could you please address this error.
Thanks and Regards,
Nilesh
Apache Load calculation error
Re: Apache Load calculation error
For the no corresponding element error the problem is caused by an 'element' on one common adjacency not appearing in both rooms. This is likely caused by the geometry changing and not being refreshed/rebuilt.
To identify/resolve:
1) Go to ModelIT.
2) Type 'rebuild' into the key-in field. (or select rebuild from Settings>Model)
3) Type ‘ClipOpenings’ in the same box
4) Type 'rebuild' again
5) Move back to ApacheSim and try running the simulation again.
If that doesn’t work then perform a check on the geometry in ModelIT by selecting Settings>Model>Intersections & Surfaces. This will produce a report detailing any issues with the geometry (intersections etc.. ) so you can fix them.