With an open top hung window, you achieve a rectangular opening at the base and two triangular openings at each side.
When establishing the free area of the window should the triangles be included for?
CIBSE AM10 seems to provide evidence either way. On Page 56 it suggests it should be in the
i.e. just the rectangle.plane normal to the flow path
But on page 22, we have
suggesting these should be included.With top hung vents, for example, the triangular opening each side of the open window is significant
Does anyone know the correct input IES is looking for?
Thanks
Ross

