ASHRAE PRM - HVAC Loads Low
Posted: Wed May 18, 2016 10:11 pm
I’m working on an early phase LEED/ASHRAE PRM model.
The building loads (both baseline and proposed) calculated are too low to be believed. I work at a Mechanical Engineering firm and have 10 years energy modelling experience and 5 year HVAC design experience. The loads as simply lower than any expectations.
My, inputs, and the PRM report indicate that the internal loads inputs seem reasonable:
Lighting = 0.94 w/sf
Receptacle = 0.45 w/sf
People = 275 sf/ppl
But the load reports indicate the autosized design flow is 0.3 cfm/sf - 0.4 cfm/sf and the cooling load is between 13 and 15 btuh/sf (800 - 920 sf/ton).
These HVAC loads are simply too low. No practicing mechanical engineer is ever going to size his units this low. I do not believe it’s appropriate to size the ASHRAE Baseline Units this low. My (and industry) expectation is about 0.75 – 1.0 cfm/sf and ~400 sf/ton.
In fact, since the min turndown flow for the Baseline VAV system is 0.40 cfm/sf, it is effectively a constant volume unit.
What could be causing such low load results?
The building loads (both baseline and proposed) calculated are too low to be believed. I work at a Mechanical Engineering firm and have 10 years energy modelling experience and 5 year HVAC design experience. The loads as simply lower than any expectations.
My, inputs, and the PRM report indicate that the internal loads inputs seem reasonable:
Lighting = 0.94 w/sf
Receptacle = 0.45 w/sf
People = 275 sf/ppl
But the load reports indicate the autosized design flow is 0.3 cfm/sf - 0.4 cfm/sf and the cooling load is between 13 and 15 btuh/sf (800 - 920 sf/ton).
These HVAC loads are simply too low. No practicing mechanical engineer is ever going to size his units this low. I do not believe it’s appropriate to size the ASHRAE Baseline Units this low. My (and industry) expectation is about 0.75 – 1.0 cfm/sf and ~400 sf/ton.
In fact, since the min turndown flow for the Baseline VAV system is 0.40 cfm/sf, it is effectively a constant volume unit.
What could be causing such low load results?