Trouble applying Internal Loads

ApacheCalc – Heat loss/gain calculations using CIBSE procedures to determine design heating/cooling loads.
ApacheLoads – Design heating/cooling loads calculations using ASHRAE Heat Balance Method.
Post Reply
bennybear
VE Newbie
VE Newbie
Posts: 1
Joined: Tue Nov 25, 2014 7:49 pm

Trouble applying Internal Loads

Post by bennybear »

Hi everyone,

I am new to IES, and I am trying to apply internal gains to run a load calc simulation.
The way that I am currently approaching it:
1) Creating Thermal Template in Building Template Manager
2) Opening up Apache
3) Assign Room Thermal Template
4) Query to make sure Thermal Template is assigned and internal gains are listed

After the Query, the gains are listed and everything seems ok, but then when I do the load calc I get 0 for internal gains.

Am I doing something wrong??
Duncan Cooke
VE Newbie
VE Newbie
Posts: 1
Joined: Mon Dec 08, 2014 3:33 am

Re: Trouble applying Internal Loads

Post by Duncan Cooke »

Are you sure the room cooling profile is not set to "Off Continuously" or the diversity isn't set to 0?
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: Trouble applying Internal Loads

Post by Complex Potential »

Hi Benny

If you are doing a CIBSE heating load analysis then internal gains are omitted as part of the methodology. If you are doing a cooling analysis or a full ApacheSim dynamic simulation then the internal gains should be showing up under vista.

CP