Baseline model doesn't include adjacent buildings

Post Reply
adrian_t
VE Newbie
VE Newbie
Posts: 8
Joined: Thu Jun 18, 2015 10:19 am

Baseline model doesn't include adjacent buildings

Post by adrian_t »

Hi,

I've noticed that the baseline model, when generated, does not include the adjacent buildings drawn in the proposed model. Is there a way to include these since I can't seem to be able to use ModelIT on the baseline model to modify it in any way.

Thanks!
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: Baseline model doesn't include adjacent buildings

Post by PCully »

Hi,

I believe the 2007 Navigator will exclude any shading objects whereas the 2010 Navigator should retain these in the Baseline building so they can be include din SunCast solar shading calculations

Phil
IES Worldwide Technical Support
farahghanem
VE Professor
VE Professor
Posts: 147
Joined: Tue Sep 08, 2015 8:41 am
Location: Abu Dhabi
Contact:

Re: Baseline model doesn't include adjacent buildings

Post by farahghanem »

Just as phil said, ASHRAE 90.1-2007 requires that no shading effects are considered for the baseline, unlike ASHRAE 90.1-2010
Image