Error in Simulation! "Surface temperature instability in room"

Posted: Fri Jul 15, 2016 1:50 pm
by JulesAA
Hi,

I tried to simulate a simple building and the following error appears:

Error: Surface temperature instability in room CL000000. Possible
remedies: add thermal capacity to construction CEIL-D; reduce time
step; set control radiant fraction to 0; check gain and ventilation levels;
reduce MacroFlo opening areas.


I tried to run the simulation after deleting room CL000000, but the same problem occurred then for the next first room in the list. So, I understand that the problem is more general, not only of this specific room.

I tried all the potential remedies, but nothing happened.

Note that the geometry and the templates were imported and assigned from another project that I created, where the simulation can be run normally!

Please help!

Re: Error in Simulation! "Surface temperature instability in room"

Posted: Sun Jul 17, 2016 12:18 pm
by farahghanem
this usually happens when you have lightweight constructions assigned and try to run a simulation with a time step too wide to properly calculate the thermal transfer.

Check your constructions and try lower sizing and simulation time steps.

Re: Error in Simulation! "Surface temperature instability in room"

Posted: Tue Jul 19, 2016 8:13 pm
by JulesAA
Thank you!