Hello,

I have a rather simple question

I want to set two different setpoints for a room. More specifically:

21C when the room is occupied (i.e. 0:00-8:00 and 17:00-24:00)

and

13C when the room is unoccupied (i.e. 8:00-17:00)

Could anyone please show me how? Making modulating profiles, using the upper setpoint did not work..

In addition, will it make any difference if I want to use different heating periods for weekdays and weekends?

Than you in advance :)

Re: How to define two heating setpoints

Posted: Tue Aug 02, 2016 3:07 am
by NebK22
Hi Jules,

That is an interesting occupancy period, what kind of building is this?

As for the schedule that you've mentioned, you need to use an Absolute profile instead of a modulating profile. See image below (in Fahrenheit)

Image

In regards to the different heating periods for weekdays and weekends, yes it will make a difference. After creating a daily profile, you have to assign it to a weekly profile in order for it to be used in IES. In the weekly profile, you can assign different daily profiles for (M-F) and the weekends.