Hi,
I'm trying to setup heating and cooling profiles for a space which requires close(ish) control, and more importantly cannot experience large fluctuations within a 24 hour period.
The heating / cooling control (24 hours a day and all year round) is to be such that:
- Internal temperature of 16-24°C with cumulative fluctuations of no more than 3°C each 24 hours.
- Internal relative humidity of 35-60% RH with cumulative fluctuations of no more than 20% per 24 hours.
I've looking through all the guides I can find and nothing I can see is relatable to this requirement....any help would be greatly appreciated.
Thanks,
Gordon
Heating / Cooling Profile for close(ish) control
-
farahghanem
- VE Professor

- Posts: 147
- Joined: Tue Sep 08, 2015 8:41 am
- Location: Abu Dhabi
- Contact:
Re: Heating / Cooling Profile for close(ish) control
why not just set a constant temperature and humidity level within the range you specified? Doing that should provide your spaces with the set-point parameters with minor fluctuation depending on how well your HVAC system is configured.
If you need to vary the internal conditions for each day, then you would need to go to the profiles menu in Apache, and edit the daily profiles for your system and set-points.
If you need to vary the internal conditions for each day, then you would need to go to the profiles menu in Apache, and edit the daily profiles for your system and set-points.