Hi,
Is there a option in Vista pro, where we could find out detailed conduction loads through different components of the room.
For example, In Vista I could see only Total External conduction gain of room.
But I could not find an option where I can find the different elements of this load.. like gain through different walls, roof, floor etc..
Would really appreciate the help..
Thanks..
Detailed Conduction loads through different components of the space
-
bharathbnayak
- VE Newbie

- Posts: 1
- Joined: Fri Jan 13, 2017 12:54 pm
-
farahghanem
- VE Professor

- Posts: 147
- Joined: Tue Sep 08, 2015 8:41 am
- Location: Abu Dhabi
- Contact:
Re: Detailed Conduction loads through different components of the space
Yes, this is possible. When you run your simulation, click on Simulation Output button and check the detailed external/conduction gains box. The results will show you conduction through all building envelope elements.