BUG: Changing Chilled Water Loop Capacity Changes Chiller Rated Capacity

Post by MatthewSteen »

Changing:

Chilled water loop > Design parameters > Chilled water loop capacity

Will change:

Chiller set > Electric water cooled chiller > Rated condition > Cooling capacity
Building Performance Engineer | Ambient Energy | http://ambient-e.com/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
farahghanem
VE Professor
VE Professor
Posts: 147
Joined: Tue Sep 08, 2015 8:41 am
Location: Abu Dhabi
Contact:

Re: BUG: Changing Chilled Water Loop Capacity Changes Chiller Rated Capacity

Post by farahghanem »

not a Bug. The chiller capacity is a percentage of the total chilled water loop capacity.

For example:

If you have 1,000 kW chilled water loop capacity and 2 chillers serving your building, then the total chillers capacity will be equal to 1,000 kW. They can be split to 50/50 or 70/30...etc