Changing:
Chilled water loop > Design parameters > Chilled water loop capacity
Will change:
Chiller set > Electric water cooled chiller > Rated condition > Cooling capacity
BUG: Changing Chilled Water Loop Capacity Changes Chiller Rated Capacity
-
MatthewSteen
- VE Graduate

- Posts: 51
- Joined: Mon Nov 17, 2014 5:43 pm
- Location: Denver, CO, USA
BUG: Changing Chilled Water Loop Capacity Changes Chiller Rated Capacity
Building Performance Engineer | Ambient Energy | http://ambient-e.com/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
-
farahghanem
- VE Professor

- Posts: 147
- Joined: Tue Sep 08, 2015 8:41 am
- Location: Abu Dhabi
- Contact:
Re: BUG: Changing Chilled Water Loop Capacity Changes Chiller Rated Capacity
not a Bug. The chiller capacity is a percentage of the total chilled water loop capacity.
For example:
If you have 1,000 kW chilled water loop capacity and 2 chillers serving your building, then the total chillers capacity will be equal to 1,000 kW. They can be split to 50/50 or 70/30...etc
For example:
If you have 1,000 kW chilled water loop capacity and 2 chillers serving your building, then the total chillers capacity will be equal to 1,000 kW. They can be split to 50/50 or 70/30...etc