Is there a way to specify light gains per individual room?

Post by iggleton »

All my rooms are are using the light gain defined by the lighting templates I defined earlier in building template manager. For example, all offices are using 12w/m2 based on the 'classroom lighting' template I defined. But since having conducted a lighting schedule I know the light gains per individual room; some offices have more than 12w/m2 in lighting gain and some less. Can I edit this information in apache per room or do I have to create a separate template in building template manager for each individual office?
wyliecoyote
VE Student
VE Student
Posts: 40
Joined: Thu Jan 22, 2015 3:26 pm

Re: Is there a way to specify light gains per individual room?

Post by wyliecoyote »

Hi,

Yes, you can edit per room.

If you find the "room query" button in apache you can overide anything in the templates.

Just un tick the template box beside whatever variable you wish to change.

The icon looks like a box with a question mark above it.

Regards