Room Loads Report
Posted: Wed Jan 30, 2019 2:31 pm
by daki
Hello fellows,
Can someone tell me where do Room Setpoint (design) and Room (actual) temperatures in the Room Loads Report are coming from and to which parameters are linked to (see below)?
Thanks!

Re: Room Loads Report
Posted: Fri Feb 15, 2019 10:45 am
by Rhind
Hi,
I believe that Room Setpoint (design) comes from either the set point set in space data or the HVAC System Parameters dialog depending on whether an HVAC System is used to model the room.
Room (actual) comes from the air temperature variable in the results file at the reported peak time.
It looks like you might have your heating operation profile set to 'off continuously'.
Re: Room Loads Report
Posted: Mon Feb 18, 2019 12:26 pm
by daki
Thanks Rhind, much appreciated. This room is set on OFF continuously for heating mode. I asked the question because I have seen a lot of discrepancies between the report and what is actually set in the HVAC system so I am trying to figure it out where it is actually coming from. If there's a prototype HVAC system it's going to take the setpoint that's in the system parameters configuration, but if there is not then it will return the setpoint value from the space condition settings if I understood you correctly?
Re: Room Loads Report
Posted: Fri Feb 22, 2019 9:27 am
by Rhind
Yes, that's right.