Hi,
I am doing simulation for passive house for my thesis.
I need the Uwindow=0.6 W/m2K
I have triple glazed low e argon filled glazing. 6 mm pane with 18 mm filled argon spacing.
I want to enter the right parameters of transmittance, emissivity, reflectance and shading to reach this U value.
please advise.
which parameters should I change and which I should leave untouched?
I understood that the low emissivity coating is applied on the 2 &4 panes .
The transmittance is the VL transmittance?
thank you in advance
R.K.
passive house glazing parameters
-
RossThompson87
- VE Professor

- Posts: 202
- Joined: Mon Feb 13, 2012 8:56 am
Re: passive house glazing parameters
Hi R.K.
After numerous attempts, I have never been able to get the IES constructions to align perfectly with provided data.
I think there are various different methods for calculating g-values etc.
Common practise tends to be to get it as close as possible then ensure that the u-value and g-value are correct, and thermal mass is accurate.
Ross
After numerous attempts, I have never been able to get the IES constructions to align perfectly with provided data.
I think there are various different methods for calculating g-values etc.
Common practise tends to be to get it as close as possible then ensure that the u-value and g-value are correct, and thermal mass is accurate.