Steady State Heating Plant Load Vs. Heating Plant Sensible Load

Detailed simulation and calculation results viewer.
Post Reply
BFarren
VE Newbie
VE Newbie
Posts: 4
Joined: Fri Mar 20, 2015 3:52 pm

Steady State Heating Plant Load Vs. Heating Plant Sensible Load

Post by BFarren »

I would like to understand what the difference is between the Steady State heating Plant Load and the Heating Plant Sensible Load.

The vista user guide says the Heating Plant Sensible Load is the sensible heating supplied to the room and is calculated from the Steady State Heating Plant Load by application of an intermittency factor.

Does anybody have an understanding of what this intermittency factor is? (i.e what its value is and how it is determined)

Which figure is the appropriate one to use for plant sizing?
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: Steady State Heating Plant Load Vs. Heating Plant Sensible Load

Post by PCully »

IES Worldwide Technical Support
Post Reply