IS there a quick way to assign Aux Vent to multiple rooms at a time?

I'm currently doing this by changing the room templates, which is slow.

The intention is to add mechanical extract at a set rate (10L/s) to many different rooms.

Any help would be appreciated!

Re: Assigning auziliary vent to multiple rooms

Posted: Tue Dec 19, 2023 3:47 pm
by Terence
Hi Bernard,

I would suggest using Tabular Space Data > System tab. This is a lot faster when changing room parameters. There is also Tabular version of Building Template Manager too which should also speed up making these changes.