Re: Construct DXF and wind loading
Posted: Fri Oct 30, 2009 9:31 am
As long as the Separation distances have been defined to take account of the gaps between walls and ceilings/floors then all modules will treat the adjacencies properly. If any internal surface is flagged by ModelIt as having an external adjacency then you should review the distance as thermally these will be considered with external air at the boundary.
Aesthetically, there is no quick way to remove the gaps between rooms if you have built the model this way. In future you may wish to attach the dxf but then manually trace over it following the convention of outer surfaces for external walls and centreline for internal partitions then define your Constructions with the appropriate thicknesses and use Inner Volumes in ModelIT to get a true representation of room areas/volumes.
Hope this helps for future reference,
Phil
Aesthetically, there is no quick way to remove the gaps between rooms if you have built the model this way. In future you may wish to attach the dxf but then manually trace over it following the convention of outer surfaces for external walls and centreline for internal partitions then define your Constructions with the appropriate thicknesses and use Inner Volumes in ModelIT to get a true representation of room areas/volumes.
Hope this helps for future reference,