I know formula SSEER but i dont know how to calculate cooling delivery efficiency?
i ru n model with EER=12 SEER=14.96 and SSEER=6 and HRP=10% ,
results shows that auxilary consumption is greater than Cooling plant consumption
What SSEER indicate
-
rohanrawte
- IES Staff

- Posts: 3
- Joined: Fri Mar 13, 2009 5:35 am
- Location: Pune
- Contact:
Re: What SSEER indicate
The relationship between the terms is given by the following equation:
SSEER = EER * CDE / (1 + (EER + 1)*HRP)
This can help you get the CDE number that you are looking for.
Are the numbers for auxiliary consumption input correctly? You may have a large number there by default which may not be the actual consumption in the building.
Hope this helps,
Regards,
Rohan
SSEER = EER * CDE / (1 + (EER + 1)*HRP)
This can help you get the CDE number that you are looking for.
Are the numbers for auxiliary consumption input correctly? You may have a large number there by default which may not be the actual consumption in the building.
Hope this helps,
Regards,
Rohan