Plug-in adds extra lines to model

Posted: Wed Apr 28, 2010 9:10 am
by jerry
The problem I am having is with a building I have drawn in Sketchup which I am now importing into IES via the plug-in.

The building has 4 floors.

When the model arrives in the VE, it is broadly OK, but contains a number of additional diagonal lines which are not present in the SU model. These cannot be removed.

Jerry

Re: Plug-in adds extra lines to model

Posted: Wed Apr 28, 2010 4:55 pm
by PCully
Hi Jerry,

Glad you got your account activated to start posting on here - I've got your SketchUp project so will take a look and hopefully be able to explain the extra lines you are seeing.

Phil

Re: Plug-in adds extra lines to model

Posted: Sat Feb 18, 2012 3:50 am
by srang
Hi, I have the same issue as well each time when exporting a floor with multiple sub-rooms (especially when they are in the centre zone of a larger space e.g. liftcore) into IES ModelIT.

Why are there diagonal lines appearing? These I assumed are intersecting lines
Is there a solution to prevent these lines from appearing?

Please advise

Re: Plug-in adds extra lines to model

Posted: Mon Feb 20, 2012 1:34 pm
by PCully
Hi,

What you have described sounds like a room in a room or donut scenario, we don't allow this and the extra diagonal line after import to VE is a symptom. You should look to split up the surrounding room into two rooms so you don't have one volume inside another in this way, when you partition the surrounding room you can make the surface a "hole" so it doesn't impede airflow or heat in any way.

Phil